If I have a motor of 1 MW with 6.6 kV, running at 35% load,
how can I save energy without reducing the load?
Answers were Sorted based on User's Feedback
Answer / mohammad a.monem salama abu se
BY REDUCING THE FREQUENCY
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
You can not lower the load ,capacity, and voltage. To save
energy ,you are left with only reduction of line current to
lessen the I^2R losses.The pf of motor is highest at
full ,or nearly full load.At 35% load ,the pf is less and
hence, the line current is more than required to take the
load (HP)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / maheshbabu calicut
by installing VFD(variable frequency drive)we can vary the speed of induction motors.at 35%load you can run the motor at low speed hence saving power
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Replace the motor with one of lower rating.
| Is This Answer Correct ? | 1 Yes | 1 No |
some basic standard questions on transformer.
what is the formula for transformer oil?
why ac current do not save
why generator one end side star neutral point given? if this point not given what happen?
How convergengr of nr method is not dependent on selection of slack bus and how gauss siedel method depends?
1) What is difference b/w impedence relay and differential relay? 2) what are substations equipments? 3) what is difference b/w circuit breaker and isolator? 4)what are the types of circuit breakers? 5) which medium is mostlty used in circuit breakers and why it is used?
can any one suggest paper presentation topies for electrical engg?
How to control the dc motor in ac supply without thyristor circuit?
what is the minimum winding resistance of 30hp compressor, to run or to switch on
how many types of ct retio
at work we have a 3 phase motor but on testing one phase isnt getting a reading. it runs 24 hours a day all week. stops and starts well no noise or heating. the phase isnt down to earth.is it just a bad meter reading or not? phases one and three came up with a resistance reading of 0.4 but phase 2 couldnt get anything shows up as open circuit.
what is the difference between earthing and grounding of electric circuits
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)