Hi friends, from Aug 4th onwards iam getting spikes for
analog inputs in our DCS for a period of 800ms. I throughly
checked every thing, finally i found that the DI, DO's from
MCC panels shields are terminated in the Signal Earth where
Analog Input signals shields are terminated. Is there any
problem with this type of termination?. i checked the
induction voltage from MCC and getting around 25VAC, please
suggest me in this concern. Our plant is 8months old only.
DCS is Siemens Make Simatic PCS7, and the transmitters are
Yokogawa make.
Answer / sankarithi
Hi Friends only problem is due to earth pit. I throughly
checked every thing, finally i found that the Earth pit
totally became dry. I serviced the pit,Now there is no
spikes.
Is This Answer Correct ? | 4 Yes | 1 No |
, Instrument Index, P&ID review, I/O schedule, datasheet, DCS / Analyzers specifications, loop diagrams, hook-up drawings.
What is the differences of Level swich( LS ) and Level Transmitter(LT)
i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?
what is effect of specific gravity in differential level transmitter , explain formula related with this .
0 Answers Flour Tech Engineers (P) Ltd,
I have energy meter for educational project having 0.5s class but my friend need 0.2s class meter , which one is good for that purpose and what is the actual difference of that two classes , need very easy example also.??
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
how we can calibrate level transmiiter in field?
What is the use of GMV in turbine?
0 Answers Hamsco, Maruti Suzuki,
Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?
What is the difference between local indicator(flow) and flow indicator?
What's the difference between cold loop test and hot loop test?
how to calculate interface capelary level transmetar lower S.G.0.54 and uper S.G. 0.26 and h=490 mm