what is main difference between live tank and dead tank
current transformer?
Answers were Sorted based on User's Feedback
Answer / samiran bairagya
Following are the advantages of Live Tank over dead Tank :
a) The Primary conductor is short than (in live tank CT) than the Dead tank CT which gives better Rigidity and gives high short circuit current withstanding capability and reliability.
b) Primary winding is uniformly distributed around Core, Hence CT is truly low reactance type, which has inherent better transient performance.
c) Due to shorter length and the tank being live the major insulation is not over the high current carrying primary, which is the main source of heat (as in the case of Dead tank type design.) the insulation does not get heated up while dissipating the heat generated. This facilitates much superior thermal stability of insulation and longer life
| Is This Answer Correct ? | 20 Yes | 8 No |
Answer / mukesh singhal
Voilent failure of dead tank CT's results in consequential damage of nearby equipments and fire in close visinity in ground.
| Is This Answer Correct ? | 1 Yes | 0 No |
What is advantages of ungrounded neutral?
What are the different types of transformers?
why efficiency of generator is greater than motor?
1)we r having one problem .one dry type transformer(6.6KV/433V)is taking high magnetizing current on delta connected HV side of "U" phase when compared to other two phases.could any body tell the reason why it is happening? 2)why CT secondary side protection core has got higher winding resistance when compared to that of metering core of same CT?
In power transformer YnD0 Vector Group is possible or not? if possible, what will be the vector diagram and what are the conditions?
how to work droop ct in generating station
Explain about p.t?
Can we use HRC Fuse inplace of Semiconductor fuse?
During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?
When a 25kV line touches the train, will passenger get shock?
what is mind in cable
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)