Capacities of the same transformer with a paricular
cooling and wihout it, in MVA
Is This Answer Correct ? | 18 Yes | 7 No |
Answer / k.prakashchandra
In continuation to my reply ,I wold like to give an
example.We have one BHEL 220/110 KV Tr with ratings 60 MVA
in ONAN ,80 MVA in ONAF and 100 MVA in ODAF .This Tr has
radiators,cooling fans and oil pumps.
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / galib ali
Transformers are desgin to continuous work of 80% of rated capacity. Hence it means 20mva ia full load capacity and 16mva is continues rated capacit.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / shahriar
full load capacity n max. Capacity
of the same tr.
Is This Answer Correct ? | 3 Yes | 3 No |
what is the difference between OSR and BUCHHOLZ relay of transformer?
1 Answers Bhushan Power Steel,
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
what is function and advantage of double delta winding in induction generator?
what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance
Mention the disadvantages of low power factor?
why transmission line towers are longer than communication line towers?
The normal highest generated voltage in India is a) 6.6KV b) 132KV c) 11KV
What is the formula to calculate distribution transformer De-rating on iron losses basis
why in transformers voltage given is in the multiple of 11
why not use capacitor in Dg sets.
why ELCB's are not useful for operation theater equipments ?
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s