I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
What is solenoid valve? Where it is used?
working principle of lvdt?
How works weighfeeders in cement industry? what is the working principle?
What is the difference between sdv and bdv ?
Describe how to calibrate various types of instruments and transmitters using ISA industrial consensus standard techniques.
What is voltage regulator?
What is the difference between modbus,fieldbus & profibus
How servomotor controls throttle valve of TURBINE?
what is the working principal of pribe
what is difference between positioner and position transmitter in control valve
in instrumentation why we are using 4-20mA , why not voltage ? if somebody design a instrument which works on voltage then can we use that instrument?
What is an analog input - output , digital input - output . Any example ???? How they r known its ai-ao or di - do