I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.



I have observed in field instrumentation work... I remove the fuse of an analog transmitter then i..

Answer / carl_ellis

Reason: ground current added to loop current through a
ground created by moisture.

The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.

When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.

Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.

http://www.piecal.com/products/evolution/334Plus_mA.php

Carl Ellis
Measure First

Is This Answer Correct ?    3 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is solenoid valve? Where it is used?

0 Answers  


working principle of lvdt?

2 Answers  


How works weighfeeders in cement industry? what is the working principle?

0 Answers  


What is the difference between sdv and bdv ?

1 Answers  


Describe how to calibrate various types of instruments and transmitters using ISA industrial consensus standard techniques.

4 Answers   Reliance,






What is voltage regulator?

0 Answers  


What is the difference between modbus,fieldbus & profibus

0 Answers   NSL,


How servomotor controls throttle valve of TURBINE?

0 Answers  


what is the working principal of pribe

0 Answers  


what is difference between positioner and position transmitter in control valve

2 Answers  


in instrumentation why we are using 4-20mA , why not voltage ? if somebody design a instrument which works on voltage then can we use that instrument?

6 Answers  


What is an analog input - output , digital input - output . Any example ???? How they r known its ai-ao or di - do

4 Answers   Torrent Pharma,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)