How to calculate battery back up time for a 400 AH battery
bank installed in telecom shelter for a load of 20 Amps and
time taken to fully charge this battery bank?
Answers were Sorted based on User's Feedback
Part -I:
400Ah Battery means the battery can supply a DC load of 400
Amps for a duration of 1 Hour until the battery gets fully
discharged. so if you are using the battery to supply the
above mentioned load of 20 Amps the battery can work for
400/20 = 20 Hours. provided the 20Amps is a Direct load
connected to the Battery. if you use the battery for a
inverter or UPS to suplly an AC load of 20 Amps. then the
duration is different.
Part - II:
For charging any battery we have to provide a voltage that
is slightly (5% - 10%) higher than the Battery terminal
voltage. The duration of charging can be known by the same
process as above. A 400Ah gets charged in 1 Hour provided
the charging source is capable of supplying 400 Amps to the
Battery. But normally the current of the charging source
will be limited to a lesser finite value. so if you can
know the maximum load the source can supply you can easily
calculate the duration required for the battery to get
fully charged.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / dharmendra kumar gautam
20hours for fully charged of 400ah battery bank
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / suyog
if we connected many cells (24) of 200Ah then how i calculate its back up for 10Amp load
Is This Answer Correct ? | 3 Yes | 0 No |
Why the rotor winding is short circuited of induction motor
For a 500 MVA 400/220/33KV transformer following data given HV power = 500 MVA IV power = 500 MVA LV power = 5 MVA If input power is 500 MVA then how output power is (500+5)MVA. Can anyone help
1. If we apply dc supply to the primary winding of transformer it will be burnt out. similarly dc supply is given to field winding of syn. motor and armature winding of dc motor, they are safe. (Remember both windings inductive nature) what is the reason behind that?
WHAT IS AIR GAP VALUE IN MM FOR A 11KV BUSHING OF 11KV/440V DISTRIBUTION TRANSFORMER. AND AIR GAP VALUE OF 25 KV BUSHING OF AT TRANSFORMER OF 25 KV TRACTION. WHAT IS THE CALCULATION FOR THE AIR GAP PERMITTED FOR BUSHINGS AT DIFFERENT VOLTAGES.
What are the applications that use Solid State Drives in your home?
what is differnce between oil transformer & dry type transformer ???????????
how to calculate Amp, 2 different Amp of batteries? Example: No. of Batteries = 2 Battery voltage = 12V 1st Battery rating = 17AH 2nd battery rating = 30AH between parallel connection then output volt 12v Amp?
Interchange 7 and 6 ,÷and× 36×7+4-7×3
how much rating of fuse and MCB should be used for a load consisting of 6KW and 18KW inductive load?
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
I completed iti in2004 I was worked in A grade contractor can I get c licence
what is the effect of constant power factor to the voltage regulation