Answer / ganeesh jain
There are earthed and unearthed cables for earthed and unearthed systems respectively.
Here, 1.9/3.3 kV = Uo/U = Phase to Earth Volt / Phase to Phase
1.9 X 1.732 = 3.3
Previously our systems were of small ratings and hence the short circuit faults were less and therefore lesser insulations were required for conductor. Whereas in advancement of time in modular system, huge fault currents are present and hence the insulation level on cables.
In earthed systems, Phase to earth voltage is 1.732 times the phase to phase voltage, where as in unearthed systems, phase to earth voltage can be equal to phase to phase voltage.
Therefore in earthed system ,stress on conductor to armour is 1.732 times lesser than the stress on conductor to conductor and hence lesser insulation is required between conductor and armour while in unearthed systems, since Ph-Earth voltage can be same as that of Ph-Ph voltage therefore the stress between conductor and armour will be more and hence the insulation.
Therefore manufacturers have designed 3 insulation classes for cables as per system design.
Insulation Class:
1. 100% : For solidly earthed systems, or on any system where the protective device will clear earth faults within 1 minute.
2. 133% : For systems where the protective device is expected to clear earth faults within 1 hour, and is typically specified for high impedance earthed or unearthed systems.
3. 173% : For systems where the time to clear an earth fault is indefinite. This is typically recommended for unearthed or resonant earthed systems.
In simple logic the 11 KV earthed cable is suitable for use in 6.6 KV unearthed system. The process of manufacture of cable is same. The size of cable will depend on current rating and voltage level.
Voltage Grade (Uo/U) where Uo is Phase to Earth Voltage & U is Phase to Phase Voltage.
Earthed system has insulation grade of KV / 1.75 x KV.
For Earthed System (Uo/U): 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV, 12.7/22 kV and 19/33 kV.
Unearthed system has insulation grade of KV / KV.
For Unearthed System (Uo/U): 3.3/3.3 kV and 11/11 kV.
3 phase 3 wire system has normally Unearthed grade cables and 3 phase 4 wire systems can be used earthed grade cables, insulation used is less, and cost is less.
Is This Answer Correct ? | 9 Yes | 0 No |
The metal sheath is earthed or unearthed. 1.9/3.3 and
3.8/6.6 are phase/ line voltages and are 3 core
cables.3.3/3.3 KV means 2 core cable for single phase
supply ,as neutral is present earthing is not necessary.UE
means unearthed E means earthed
Is This Answer Correct ? | 14 Yes | 9 No |
how we can check that any motor is faulty may be single phase or three phase?
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.
What is the difference between KW & KVA ?
what are the advantages and disadvantages of oil filled cables over XLPE cables
What is SFU ?
which one is dangerous AC Power r DC Power for Electrical Shock ?
how to select the cable size? any formula to calculate cable size?
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
How dc generators direction can be reversed ??
2 Answers GPSC Gujarat Public Service Commission,
how to calculate full load current of transformer & induction moter ?
If load current is 70amps or 50amps what range of CT to install for ampere metering