In split range control, we will control 2 outputs with time
interval. Eg :(with 4-20 ma signal, for 4-12 ma we are
operating one control instrument like valve & for 12-20ma we
are operating other control instrumet (other valve). If we
get a signal of 15ma to first instrument (Valve 1), what
will happened to the first valve, and if we get signal above
20 ma to 2 valve what will happened ?
Answers were Sorted based on User's Feedback
Answer / kyle condran
It depends on the setup the 2 above post both correct the following scenario can also be seen sometimes.
Valve 1 set for 4-12mA (100% open @ 4mA and 0% open at 12mA)
Valve 2 set for 12-20mA(100% open @ 20mA and 0% open at 12mA)
For example if you have a temperature control with 2 valves one controlling steam and one controlling chilled water, going into a heat exchange process, when we want to increase temp out of heat exhanger contol signal goes up towards 20mA chilled water valve closes and steam valve opens. when we want to cool the process down the opposite happens and the control signal falls towards 4mA the steam closes and chilled water valve opens.
so 4mA is full on chilled water 20mA is full on steam 12mA is both closed.
lets assume fail open cooling / fail closed heating valve.
as for 15mA on valve 1 depending on where the split range is done, ie controller or valve.
for our example if done in valve it will ignore anything above 12mA and be fully closed.
above 20mA in our example will be ignored by valve 2 since it is allready at 100% at 20mA.
see http://www.contek-systems.co.uk/Documents/split_range_control.htm for the first 2 post
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / romeo
The first valve will open fully open (100%) and the second
valve will open at about 37.5% only.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pramod suwalka
1. at 15 ma signal first Valve open fully.
2. at 20 ma signal Both Valve open fully.
Is This Answer Correct ? | 1 Yes | 5 No |
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
why to use 3 wire at RTD ? what's the reason for common wire ?
What is the exact output of eddy current proximity probe? For vibration mesurment?
how does we do bench calibration of a differential transmitter.
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
Can anybody tell me application of PLC,DCS,SCADA.
hi! i want to know about mpse exam.
What is diffrent profibus & OFC Communication
Reasons for using current as signal
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?
What is Cu-100 and Cu-1000 ? and tell me its application ?