Explain Buccholz relay in detail.
Answers were Sorted based on User's Feedback
Bucholz relay is connected in between the manin tank and
conservator tank and in an angle, when the faults like
loose connection or heat desipation from winding occurs the
gas buble is produced in the oil. As the conservator tank
is installed above the tank level the gas buble trys to
travel to the conservator tank, in between the bucolz relay
is there the gas buble gets trapped in the bucolz relay and
it presses the flot in bucloz relay to down words and it
will activate for once in lot of faults like gas develops
if sudden major fault like short CKT it will activate
imediyetly
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / yanamadalaashok
Buchholz relay is a gas- actuated relay installed in oil-
immersed transformers for protection against all kind of
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / roysayan01
plz explain the working dude...how does the mercury buckets
actually work???
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / basavaraj patil
Buchholz relay is a gas- actuated relay installed in an oil-
immersed transformers for protection against
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anbarasandurairaj
Bukolz relay is a gas operated relay used to protect oil immeresed transformer from fault it is located between conservetor and transformer tank if there is any minor fault inside transformer relay trigger the alarm, major fault relay trigger the gripping cicuit and protect the transformer from fault.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate KA rating of C.B?explain with Formula.
design of IGBT firing circuit for 11KV
While testing LA mast,What are the parameter limits ?
what is the term of desruptive voltage
5 Answers Bhel, Energy Infratech,
L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW MOTOR STARTS WITH EARTH FAULT RELEASE
What will be the effect if I use inverter as UPS mood?
Given a ckt,the max power dissipated in the load ZL ?
what is LUX?
while doing the excitation current test on power transformer what is the value of voltage to be applied? Nomonal rated voltage or 10% of rated voltage? Is it necessary to apply on high voltage side?
Explain Even and Odd signals?
why fuse is not applicable for nutral and what will happen when it applied.
What is the difference between Surge protection device and Lighting arrester?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)