Answer / eduardo
In a delta connection you don´t have any access to the "mid
point" or if you prefer to the "neutral".
In a star connection you will have a four(th) terminal, that
you can connect to earth or use it as neutral conductor.
For example if you have a three phase power line at 15 kV,
and want 400 V and 230 V you can connect the primary in
delta (you don´t need the extra connection) and the
secondary at star. (delta- star)
Now you will have 400 V between any 2 phases and 230 V
between one phase and the star point of the transformer.
If you connect the secondary in delta you will not have 230
V, because you don´t have the 4th terminal. (delta-delta)
Please note that in star one winding of the transformer will
have 5,8 kV (10000V / sqrt(3)). In delta connection you will
have in one winding 10 kV. So verify the tension and the
connetction type of the transformer. (both primary and
secondary).
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / shahbaz shaikh
in delta-delta transformer primary side and secondary side of transformer are connected in delta fashion i,e R-Y-B are connected in triangle fashion these are generally prefer for the transmission system and here no neutral point is present and for the distribution system we use the delta star because our home appliances are work at 230v but in 3 phase we have 440v so to get the 230v we use delta primary and star secondary so by using one of phase and neutral point of star we can get the 230v.
Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate the neautral earthing conductor size for a 500kva dg set.
area control error
difference between servo motor and synchronous motor
Define damping ratio.
Why the size of transformer decreases if we increases the frequency?
5 Answers Graphics Engineering,
Hi, I'm running plastic reprocessing company where all motors are running only in delta. Due to that when I use start my 30 hp motor my transformer gets fuse. Where it happens two times a day. I gt a suggestion from a person about Automatic Power Factor Controller APFC. Is it useful for my problem??? Or is der any other way for solving this problem?? Upgrading the transformer is difficult. Pls give Me ur suggestion. Waiting for ur reply.
2 Answers Shree Lingaa Polymer,
what will happen if 11KV is given to 1.5 square mm cable connected with constant load of 10A ?what will be the condition of cable after injecting the voltage?
practicalLY what is impedence ...?
if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?
my self i am raghu working as tech.. in my college the maximum demand is 211 kva presently we are using 12kva capacitors the target power factor is .95 so what capacity of capacitor banks should i install
explain types of electric welding and its applications
Batteries used for electrical energy storage are a. Laclanche cells b. Edison cells c. Lead acid cells d.any of the above