We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?

Answers were Sorted based on User's Feedback



We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / prajeshkumarbe@yahoo.com

hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh

Is This Answer Correct ?    2 Yes 0 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / rajesh

Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .

If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue

Is This Answer Correct ?    7 Yes 6 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / n. gopala krishna

what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side

Is This Answer Correct ?    3 Yes 3 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / elango

the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...

Is This Answer Correct ?    2 Yes 2 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / deepak

you have to use softstarter for this problem.

Is This Answer Correct ?    0 Yes 1 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / rajju

Kindly check the other loads that u r connected because
there may max demand problem

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

is there any phase difference occurs while primary and secondary side mutual induction occurs?

0 Answers  


why put integration for capacitorand differation for inductance

1 Answers  


what is mean by dual digital protection in the relay field?

0 Answers   ABB,


What is GNR ? How much value of ground neutral resistance?

9 Answers  


what is first ground fault & second ground fault. This is used in rotor protection of alternator.

1 Answers  






While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply

2 Answers  


difine electrical ballast in HPSVL

0 Answers  


1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done

0 Answers  


How harmonic block test are conducted on relays ( Siemens,Areva ect )power transformer using omicron kit?

0 Answers   Siemens,


Why frequency fix in 50 Hz?

6 Answers  


Why breakers not synchronized when the synchroscope is going in the anticlockwise direction?

2 Answers  


how we can calculate chiller required ampear?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)