We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?
Answers were Sorted based on User's Feedback
Answer / prajeshkumarbe@yahoo.com
hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .
If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / n. gopala krishna
what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / elango
the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...
Is This Answer Correct ? | 2 Yes | 2 No |
is there any phase difference occurs while primary and secondary side mutual induction occurs?
why put integration for capacitorand differation for inductance
what is mean by dual digital protection in the relay field?
What is GNR ? How much value of ground neutral resistance?
what is first ground fault & second ground fault. This is used in rotor protection of alternator.
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply
difine electrical ballast in HPSVL
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done
How harmonic block test are conducted on relays ( Siemens,Areva ect )power transformer using omicron kit?
Why frequency fix in 50 Hz?
Why breakers not synchronized when the synchroscope is going in the anticlockwise direction?
how we can calculate chiller required ampear?