We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?
Answers were Sorted based on User's Feedback
Answer / prajeshkumarbe@yahoo.com
hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .
If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / n. gopala krishna
what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / elango
the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...
| Is This Answer Correct ? | 2 Yes | 2 No |
how we select fuse rating for motor?
Where should the lighting arrestor be placed in distribution lines?
What is difference between Harmonic and Non harmonic Capacitor Bank?
How can CALCULAT the current carrying capacity of aluminum and cOpper cables respective of that Sq.mm ? with formulas ?
12 Answers Bajaj, Eagle, Godawari Power and Ispat, Havells, L&T, Mascot, Polycab, SGML, Sterling Wilson,
In generally how many earthing required for power
what is the acb tripping & closing voltage.
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
How to calculate Number of Earthing Pits....???
Hello sir. if u have electical engineering exam paper then plz mail me at bhumika_1187@yahoo.co.in. i m appearing exam for HPCL.
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
what do you mean by mf of energy meter & its formula?
what is residual current....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)