what is the diff of mcb and mccb
Answers were Sorted based on User's Feedback
Answer / desingurajan
MCBs are miniature circuit breakers with optimum protection facilities of overcurrent only.These are manufactured for fault level of up to 10KA only with operating current range of 0.5 to 63 Amps (the ranges are fixed), single,double and three pole verson.These are used for smaller loads -electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection facilities of overcurrent, earth fault.it has a variable range of 50% to 100% operating current.They can be wired for remote as well as local operation both.They are manufactured for fault levels of 16KA to 50KA and operating current range of 25A to 630Amps.They are used for aplication related with larger power flow requirement.
Desingh
RAjapalayam
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / kadher.304
mcb its thermal operated and use for short circit rating of
mcb 63amp(max)
mccb is thermal operated for over load current and magnetic
oprataion for instant trip in short circuit condition.rating
of 63amp(9min)
Is This Answer Correct ? | 7 Yes | 1 No |
what is the distance maintained between the power and data cables with respect to the KVA .... plss give me the formula
Please specify the parts of VCB&ACB
which type of insulation are used on 132kv transmission line
electrical ques
In 63kva LT Distribution Box Why the outgoing of 63A kit kat is connected to 200 A link disconnector? as the output of kit kat is only 63 A?
Can we perform parallel operation of two transformers when one transformer on load?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
why using eleven's multiple for substations?
Please brief me about number of pole in alternator.In single phase alternator coils are connected in star or series. How to calculate frequency for the same.
Assume a condition such that two motors of rating 6.6kv,415v are connected to blower,so tell me which motor draw large current give appropriate reason?
WHAT IS THE CURRENT CARRYING CAPACITY OF 2.5/3 CORE HI TUFF CABLE,WILL IT SAFLEY CARRY 8.6 AMPS OVER 120 METRES,CAN YOU ALSO ANSWER WITH FORMULA FOR WORKINGS OUT ,THANK YOU 3RDYR APPRENTICE.
how many types of grounding?