Answer / raghavendran r
The reverse power relay is used to monitor the direction of
power from A.C generators, if the current in the system
being monitored is reversed, to a value greater than the
customer adjustable preset limit the relay will energise.
The adjustable trip point is 2% to 20% of input current. An
adjustable time delay of 0 to 20 seconds is provided.
Correct setting of the trip point and time delay, will
ensure protection against motoring action of the Syn gen.
An inadverdent relay is used to trip the circuit when a syn
gen has been energised or excited inadvertently.
Is This Answer Correct ? | 1 Yes | 0 No |
Generally the incandescent lamps in bathrooms fuse due to high voltage at night.What is the simple solution of this problem?
can u give me a brief idea about power line carrier communication ??
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
Difference between hopkinson and swinburne's test
what are the type of motors
what is ups Paralleling? how is load sharing at that time ? what are the things we have to note that time?
Capacitor bank require for 1000amp load
2 Answers Biodeal, Pharmaceutical,
Why does inductor is connected to dc supply? or what is the role of an inductor when connected to DC source?
What kind of maintenance is conducted for Transformer
0 Answers Gulf, UB Engineering,
What are the different types of cable jointing methods for HT and LT power cable?
what is the maximum load sutiable from earth to phase and what is the max voltage earth to phase suitable
Is it possible to make 0.75KW motor earthing from MCC panel by using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases & 1 core for Earth terminal?