In 6600/√3/110/√3v voltage transformer,how much output
voltage in open delta transformer,after removing 1-phase of
primary side on transformer?
Answers were Sorted based on User's Feedback
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V.
If all three H.V.phases are connected the voltage between secondary terminals[in series] is 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V.
| Is This Answer Correct ? | 0 Yes | 0 No |
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V[ some time even 100 or 110V].
If all three H.V.phases are connected the voltage between secondary terminals[in direct series] is 110/√3<0o +110/√3<120o=-110/√3 V<240o or oppositely connected 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V[or 110 V] for direct connection or 0 if they are oppositely connected.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is meant by Resonance what are the different types of resonance and what are uses of them?
How we select the cable rating
In EHV transmission line a neutral grounding reactor is often placed at neutral point of shunt reactors. What is the recommended protection for this neutral grounding reactor? Should I use a fast closing switch to bypass neutral grounding reactor when this protection operates?
Can we parallel lise the secondary side of the two similiar transformers with same voltage ration, imp, but with different vector groups.. ( for ex. 11 KV / 6.6KV two trfs but different vector groups can we parallelise both of them ,, what happens if we parallelise them
Name the test signals used in control system
if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm
hello freinds what is advantage and disadvantage of plc again dcs?
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
What is the need of ISOLATION Transformer?
how much amps will get from a 360/11kv line
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
What is CRT (Contact Resistance Test) for Isolators or Dis- connector Switches? Why we performed it & whats the Testing procedure.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)