In 6600/√3/110/√3v voltage transformer,how much output
voltage in open delta transformer,after removing 1-phase of
primary side on transformer?
Answers were Sorted based on User's Feedback
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V.
If all three H.V.phases are connected the voltage between secondary terminals[in series] is 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V.
Is This Answer Correct ? | 0 Yes | 0 No |
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V[ some time even 100 or 110V].
If all three H.V.phases are connected the voltage between secondary terminals[in direct series] is 110/√3<0o +110/√3<120o=-110/√3 V<240o or oppositely connected 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V[or 110 V] for direct connection or 0 if they are oppositely connected.
Is This Answer Correct ? | 0 Yes | 0 No |
Is it possible to increasing the real power generation by reducing the reactive power in power generation plants
What is voltage in two phase?
Why the TNC switch is called as Memory switch
Is KCL applicable for close circuit?
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
which is better VCB or ACB and why?
What is the classification of hydro projects based on installed capacity?
What is the difference of grounding and earthing?
what is phase to phase fault? what is line to line fault?
why single CT used in DOL starter power circuit?
what are the different pre- commissioning tests performed on distribution transformer, power cable and switchgear?????
difference between silent and non silent pole rotor?