how can we use isolator as breaker
Answers were Sorted based on User's Feedback
Answer / prasanna
Isolator is a switch which cant do the breaker function.
Breaker can trip very high voltage with provided arc
quenching ability.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sachin kumar chauhan
Basically isolator is an switch manually used to on or off
the circuit.but the bracker have many safty as short
circuit,earth folt,over load,under voltage & over voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anand yadav
The isolators are manually operated switches rated for different voltages and current and selected as per application. The isolators are of two types:
Off Load Isolator and On Load Isolators.
Off Load Isolators cannot be used to break the circuit on load, so it is provided with some mechanical or electrical interlock to avoid on load breaking, otherwise it may be dangerous for operator and the equipment.
On Load Isolator can be used to break the circuit on load but cannot substitute the Breaker.
The Breakers have remote operating features with many in built protections and so many add on protections with high breaking and making capacity.
Hence Isolator cannot be used as Breaker.
Is This Answer Correct ? | 0 Yes | 0 No |
What will be cross section area of copper conductor for carry 2000 amps & 2500 amps....sq.mm.?/
c++ write a program to use a fuction call "max"which accepts an intger arrey of size5.as an arrument and return the larger and smallest of the arrey to main without changing. the original changing of the original position of the element of the arrey.
why are the maintaine power factor and how can this control and this is how work.
What are the main Electrical IS rules?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help
can we run three phase motor by single phase? and what happens if we do this
What is the major difference between cnc and plc. why cant we use plc instead of cnc
What is meant by pilot exciter and its working?
What can be a rating of a transformer(KVA) if the load is about 1000KW?illustrate by showing formula?
How much UG cable size should i use so as to accomodate a ground + 2floors house. A 1.5ton AC & geysers(2) in each floor with lightings
How do we calculate the maximum amount of current in a 300 SQ.MM cable ?