why CT out put is 5 what ever the primary current.
Answers were Sorted based on User's Feedback
Answer / mahesh-lanco
The Main Functuion of the Insturments Transformers(Current
Transformer &VOLtage Transformers) is to Standartise the
secondary to less value. As the Relays and Circuit breakers
are designed at Very Low Values(DC).If the fault curent or
voltage is very high there is no meters manufactured for
the measurment of such high volatgaes/currents the
Secondaries of CT &PT are standartized to 5Amp and 100V
respectively
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / abhik raj
it is standard that CT sec should be 1 or 5 amp based on
partys demand.becz relay/meter are designed for the
same.otherwise it is difficult for both manufacturer/user.
Is This Answer Correct ? | 3 Yes | 0 No |
Sir we are using 250 kva DG its Diesel consumption 25 lits / hrs maximum load 160 kva now how to calculate units/ litres
How can we convert 11 kv to 440 volt without using transformer ?
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
What is disc insulator and it's application..?
What is knee point voltage?
what things to be considered when designing UPS
0 Answers Aplab, Veta Kipawa ICT Center,
If i am running of spindle at 2000rpm ,but How to spindle stop at the second I am resetting the machine in CNC machines
what is two point starter?
Shunt reactor is used in EHV Transmission line for..............?
in case of induction motor when overload condition or any short ckt. why stator winding burn not to be rotor winding
What is thermal overload relay
how to arrange the generator protection ansi 48 (loss of phase?)