how to calculate cable size, olr rating, contactor rating
and mccb rating,to below given details three phase motor
75 kw,415 v,.85 pf,50 hz?
Answers were Sorted based on User's Feedback
Answer / brakadeesh
motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =200
amp
is best.
Is This Answer Correct ? | 50 Yes | 35 No |
Answer / pvr.parthasarathi
75 Kw motor takes 134 amps full load current. But for
selecting its Cable, Contactor, OLR and MCCB, we have to
consider many other factors such as need of its operation.
Place of the Motor Control Centre and possibility of laying
the cable Wheter inside the duct, underground or in the
air. For selection of the Contactor enclosure of the
panel, its environments etc are to be taken into
consideration. So giving answer at a stretch basing on
some thumb rule is not technically qualified.
Other particulars are required.
Is This Answer Correct ? | 19 Yes | 5 No |
Answer / v.raguvaran
THE MOTOR AMP IS 130AMP.THE CABLE(USE COPPER ) SIZE SHOULD BE 45sq.mm (delta connection),35sq.mm(star delta)
OLR RATING IS (125-135) BUT STANDARD SIZE IS (130-175)ABB
CONTACTOR RATING IS 200A(DELTA),100(MAIN)-100(DELTA)-50(STAR)
MCCB RATING IS 250A
Is This Answer Correct ? | 0 Yes | 0 No |
i know> but my nglish not well> because of that i can not answer
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / rsbangra
motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =300amp
is best.
Is This Answer Correct ? | 47 Yes | 57 No |
how capacitor control the power factor/
Explain the advantages and disadvantages of hydropower plant?
1 amp means-how many electron flow per second. ?
what is Fault level? why it is calculated? how will u decide same for our plant?
why 400Hz is used for aircraft systems ?
14 Answers Cabin Crew, Jet Airways,
What happen when increese more than 50HZ fequincy.
kindly send me 11KV MV motor differential protection procedure by primary injection method.
What happens if the series current double?
Simple explanation of kirchoff's law
What is cable tray, its type, and its support?
how to save the power in company?
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?