Answer / brakadeesh

motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =200
amp
is best.

Is This Answer Correct ?    50 Yes 35 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / pvr.parthasarathi

75 Kw motor takes 134 amps full load current. But for
selecting its Cable, Contactor, OLR and MCCB, we have to
consider many other factors such as need of its operation.
Place of the Motor Control Centre and possibility of laying
the cable Wheter inside the duct, underground or in the
air. For selection of the Contactor enclosure of the
panel, its environments etc are to be taken into
consideration. So giving answer at a stretch basing on
some thumb rule is not technically qualified.

Other particulars are required.

Is This Answer Correct ?    19 Yes 5 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / v.raguvaran

THE MOTOR AMP IS 130AMP.THE CABLE(USE COPPER ) SIZE SHOULD BE 45sq.mm (delta connection),35sq.mm(star delta)
OLR RATING IS (125-135) BUT STANDARD SIZE IS (130-175)ABB
CONTACTOR RATING IS 200A(DELTA),100(MAIN)-100(DELTA)-50(STAR)
MCCB RATING IS 250A

Is This Answer Correct ?    0 Yes 0 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / mohamed-mohamed

i know> but my nglish not well> because of that i can not answer

Is This Answer Correct ?    1 Yes 4 No

how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details t..

Answer / rsbangra

motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =300amp
is best.

Is This Answer Correct ?    47 Yes 57 No

Post New Answer

More Electrical Engineering Interview Questions

how capacitor control the power factor/

2 Answers   ABB, Apollo,


Explain the advantages and disadvantages of hydropower plant?

0 Answers  


1 amp means-how many electron flow per second. ?

2 Answers  


what is Fault level? why it is calculated? how will u decide same for our plant?

0 Answers  


why 400Hz is used for aircraft systems ?

14 Answers   Cabin Crew, Jet Airways,






What happen when increese more than 50HZ fequincy.

5 Answers  


kindly send me 11KV MV motor differential protection procedure by primary injection method.

0 Answers  


What happens if the series current double?

0 Answers  


Simple explanation of kirchoff's law

2 Answers  


What is cable tray, its type, and its support?

0 Answers  


how to save the power in company?

0 Answers  


What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?

0 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)