Answer / brakadeesh
motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =200
amp
is best.
| Is This Answer Correct ? | 50 Yes | 35 No |
Answer / pvr.parthasarathi
75 Kw motor takes 134 amps full load current. But for
selecting its Cable, Contactor, OLR and MCCB, we have to
consider many other factors such as need of its operation.
Place of the Motor Control Centre and possibility of laying
the cable Wheter inside the duct, underground or in the
air. For selection of the Contactor enclosure of the
panel, its environments etc are to be taken into
consideration. So giving answer at a stretch basing on
some thumb rule is not technically qualified.
Other particulars are required.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / v.raguvaran
THE MOTOR AMP IS 130AMP.THE CABLE(USE COPPER ) SIZE SHOULD BE 45sq.mm (delta connection),35sq.mm(star delta)
OLR RATING IS (125-135) BUT STANDARD SIZE IS (130-175)ABB
CONTACTOR RATING IS 200A(DELTA),100(MAIN)-100(DELTA)-50(STAR)
MCCB RATING IS 250A
| Is This Answer Correct ? | 0 Yes | 0 No |
i know> but my nglish not well> because of that i can not answer
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / rsbangra
motor rating 75kw,so it taken full load p=1.732*v*I*cosfy
i= p/1.732*v*cosfy
=123 amp. so we requared a cable to carry 123 amp
contonious rating. so require to run motor in star delta
starter . in star delta connection load current is 58% of
line current. we require 58% of 123 amp carring capasity
cable.it is around 71 amp.generly copper cable taking 4
times current of cable rating and alluminium cable taken
1.5 times of cable ratting .so for 71 amp carring alu.
cable 50mm2 suffisent but due to high starting curent its
take 70 mm2 cable ib best.
its overload relay ratting is in range to 71 amp. it to be
60-80 amp,and mccb rating is 2.5 times of full load =300amp
is best.
| Is This Answer Correct ? | 47 Yes | 57 No |
In any plant or substation main incommer voltage RY - 415 V,YB - 400 V, BR - 387 V(in commer feed from transformer 11 Kv /0.415 KV) why found voltage differance in each phase? plant have not self power plant it is depend on outsource grid
The Source internal resitanse Rs , When equal to Load resistance RL, the maximum transfered is of _____ % of input power?
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
IDMT relay are mostly used for protection against..??? 1)Earth Fault 2)Inter turn fault 3)Overloading 4)None of the above
What are differences between Voltage, EMF & Potential difference ?
Which is the best protection in case of shortcircut fuses or mccb ?
how to conduct dc resistance test for rotor of an alternator and how to measure the rotor dc resistance value theoritically?
diffance between eletrical and eletronics?
What is the basic working principle of Tri vector meter?
in india why we not use frequency above 50 hz for distrubuting power ?
what is spadar bar .why I use in DC generator.
how a vibration switch's high signal will going to trip the motor? can u explain with some examplesand wiring diagrams?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)