WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING
INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
Answers were Sorted based on User's Feedback
Answer / kaja farkhan
Calibration is nothing but comparisonof an unknown standard
with an known standard or in other words it is known as
checking the output is proportional to the input or not.
Loop checking is nothing but the instrument installed in
the field must give the signal to the control room without
any break. First in this the continuity of the cable will
be checked from inst to JB in field side and from the JB to
control room.
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / nagabalan
Loop check used to check the Field Instruments activity and
continuity from Field to DCS/PLC.
Field Instruments forced/simulated from filed and value
will be confirmed with DCS/PLC.
For Valves,value simulated from DCS/PLC and position will
be confirmed from the field.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / safeek_psna
I NEED TO SEND THE ANSWAR ABOUT INSTRUMENTAION
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / narenkumar1985
LOOP CHECKING MEANS CHECKING THE CABLE LOOP FROM THE INST TO
MARSHALING PANEL AND TO PLC. WHEN INST GIVING O/P SIGNAL TO
CONTROL ROOM-PLC CHECKING WHETHER THE SIGNAL GOING TO
CORRECT PLC CHANNEL.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / goldknight3000
Calibration of an instrument is a comparison to a known
standard. Eg. if i need to calibrate a weighing scale, then
we need a known weight for comparison. A known standard
have to be certified by certfying body like NIST.
Loop check is a continuity test coming from/to field to
junction box and junction box to/from Control system.
| Is This Answer Correct ? | 0 Yes | 2 No |
Why do we floating DC in DC system.
why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?
Operational amplifiers
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
why we r opening HOT BYPASS valve during startup of a compressor?
what should be distance from tapping point to inallation place of instruments?
3 Answers Tasnee Petrochemicals,
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
draw the characteristics of chebyshev filter
What is an antisurge control system, how it works?
diff between neutral ,ground,phase , earthing and shielding?
IN JB CONSTRUCTION WHY WE ARE USING JUMPPER........CAN U PLEASE TELL ME.....
What is the difference bitween control net scaner and device net scaner
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)