what is the std. earthing resistance for 440V system or
m/c, 33000/440 Volt substation? What is the std.?
Answers were Sorted based on User's Feedback
Answer / abdul wajid
The standard earthing for 440V system is less than 1 ohm ,
for 33000/440V the standard earth resistance is 5 ohm
Is This Answer Correct ? | 7 Yes | 0 No |
Earthing resistance standard values:
Without Grid (Individual Earth Pit) = Less than 01Ohm
With Grid = less than 05Ohms
Is This Answer Correct ? | 0 Yes | 1 No |
which one is the most common system for secondary ditibution
1. Why a DC motor starter is called 3 point starter
21 Answers ABB, CG, College School Exams Tests, Crompton Greaves, Infosys, Siva,
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
What is the difference b/w earthing & grounding?
transformers parts & function of each parts
25 Answers Amara Raja, Bhutan Ferro Alloys Limited, Breather, Electrical, Electrical Tech, ERDA, GVK, Juniper Networks, Matrix, Mechanical, NFL, Oracle, Pyramid Plastics, RPPL, RRB, Siemens, TCS, Tulip Silk Mills,
why hv current transformers have big size ?
what happens if DC earthing and AC earthings are shorted?
why ht cable end termination don't have a gland?
why the vector group of excitation transformer is YD5(150 deg)how is this factor decided.
What is clean Earth System ?
Does outdoor isolator loose connection cause short circuit current in that circuit? if yes then how ??
Why 4 pole generator generates more power and 6 pole generates less power campare to 4 pole
2 Answers Julius Berger, Suzlon,