Answer / zan
Several variable factors are involved in the
design of earthing mat conductor.Therefore, earthing mat
for each substation has to designed individually usually.
The earthing mat has to be designed for the site conditions
to have a low overall impedance and a current carrying
capacity consistent with the fault current magnitude. The
parameter listed below influence the design of earthing mat:
• Magnitude of fault current;
• Duration of fault;
• Soil resistivity .
• Resistivity of surface material;
• Shock duration;
• Material of earthing mat conductor and
• Earthing mat geometry.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / parag shukla
It is basically depends on the soil resistivity & system
load. You can calculate the current for this load from that
calculate the conductor size & earth mat calculations
| Is This Answer Correct ? | 3 Yes | 5 No |
Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A, CT 60/5A
why can't we provide dc supply to a transformer?
if we connect a ohmmeter across shorted capacitor .what will be the reading..will it be zero or infinity
what is a,b,c,d checks diesel generator?
why in a transformer frequency remains constant? if frequency is changing what will happen?
How can maintain our H.T. motors used in cement plant. please send me procedure.
What will happen if we parallel two transformer with different %impedace?
What is a unit of gravity (Battery)
In chillers & freezers which gas will be use?
how we can check the CT & VT?
Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same office?
I have a drawing of a wound rotor induction motor for a crane. This crane motor has 5 forward speeds & 5 reverse speed implemented of course with different amount of resistance for each speed setting selected. What has got me scratching around is the fact that 8 of the 10 speed selections switch in uneven (unbalanced) amounts of resistances on each of the 3 connections to the motor's rotor.Can this be possible? I would have assumed this would produce unbalanced rotor currents and therefore vibration in the motor. I would greatly appreciate anyone's comments on this. Many thanks, Confused.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)