Electrical Design specifications
Answer / me
Greetings all,
iam working in an out door lighting design for our plant
and i calculated the total watt needed (sum of all lights)
= 53 kw, 220 volt
our power supply is 480V
so, I chosed a 75 KVA transformer dry type 480/220-127 V 3
phase 60 Hz
cable size from feeder to transformer primary = 50 mm2 (1/0
AWG)
cable size from transformer secondary to distribution panel
board = 125 mm2 (250 MCM)
distribution panel board main breacker = 250 A
So, are my calculations ok ? any changes or suggestions ?
thanks in advance
Is This Answer Correct ? | 2 Yes | 0 No |
what is a circuit breaker. Weite the types of circuit breaker.
what is the problem with single phase AC motors and how is it overcome?
WHY FEEDERS TRIP IN COLD AND FOGY WEATHER?
How to calculate impedance volt in Transformer?
exolain the star delta connection
How to put breaker in service / test position.
Why we did not feel electric shock in electric train?
Should the neutral earthing of 33/11KV D-S transformer, be connected to the earth grid?(Yes/ NO) why?
1 Answers HAL, Vijai Electricals,
what purpose to use excaiter in DG.?
Testing procedure of DG alternator stability test
in which direction real power and reactive power flow and why???????
please give some hindalco placement papers for written exam