how many types method in earth testing?
Answers were Sorted based on User's Feedback
Answer / manish parekh
Thaire is 2 method of earth testing which is carry out by
earth tester instruments.
1.Three point method
2.Four Point method
thanks
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / gaurav kdk
1 Tow point method.
2 Three point method.
3 By megger.
Is This Answer Correct ? | 2 Yes | 0 No |
Difference between megger test equipment and contact resistance meter test instruments?
effect of single phase transformer on full load current?
How can calculate thermal overload in relay?
what should be the megger test report for 11KV cable when meggered with 5KV megger , what is the resistance value we should get
A 2083kva AVR was tested, phase to ground shows continuity, what is the implications
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
My ups output shows 230 v between phase and neutral,but show zero between phase and earth.Is the system/installation is correct.If not what will be the possible reasons
What is vaccum currcuit breaker.define with cause and where be use it device?
how to use single phase supply for a three phase equipement.
State the difference between Surge Arrester and Lightning arrester,Both are same or not?
If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.
how we masure a cuurrent?