Waht will happened if reactive power increase in the line?
waht about active power increase too?
Answers were Sorted based on User's Feedback
Answer / nishad
Above answer almost correct. Eventhough I would like to add
something.
In Load current there are two components 1> active
components which is the current consuming by the custmer.
2> Recative components which is the current responsible for
the system, lead to lag / lead.
well, If reactive power is increased, PF will be lag. means
the system will carry more current for the disered out put
the same of unity PF. So our losses will increases like
more bigger size cable, breaker we need.as well as our
power system will over loaded. as reasult CU loss & Iron
loss will increase. so try to avoid that stage.
If active powre increase, then also system will over
loaded. to avoid that, share the load of particular system
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / iamdon
Reactive power flows from higher voltage to lower
voltage.Flow of increased reactive power in line
causes power factor to reduce.For fixed value of
sending end voltage, receiving end voltage drops.
Active power flows from side which has leading
voltage angle to lagging end.
Increased Active power flow causes more line losses.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ballaya
p=v*i*cos(φ),so as mentioned above,reactive power inc cosφ
inc(look power triangle) as voltage is constant so current decreases to maintain he given power
| Is This Answer Correct ? | 0 Yes | 0 No |
how capacitor control the power factor/
What descriptive information does the NEC require to be marked on all conductors?
battery spicgravity mesuserd?
EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)
In a HT switchboard where Nos. of Transformers are connected, how to decide Incoming cable size? Whether Cable should be rated for connected load or maximum demand?
What is the different between feeder & bus?
we have 3 phase 4 wire supply 230/415 V.AC and our distribution is single phase or we have all single phase 220 v,ac operated appliances. and noted the current with help of clamp meter Red to N = 20 Amps. Yellow to N = 45Amps and Blue to N = 30 Amps ( total is 95 Amps ) what will be neutral current on the main .
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
What are the causes of eddy current losses?
what is impedance in a transformer? how can i calculate it?
What is the type of electrical motor used in mining industries?
which sub is most horrible in four yr degree
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)