why Batteries & Battery chargers are used in substation?
what is the different between UPS & battery charger?

Answers were Sorted based on User's Feedback



why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / jai prakash

generally we gave dc supply to the all protective equipment
like relays ,indicators , and for all controlling devices
through batteries in substation .

Battery Chargers are basically Automatically Stabilised D.
C. Power Sources meant to feed the connected load and
simultaneously trickle (float) charge the connected Battery,
thereby maintaining it (Battery) continuously healthy &
ready to feed the load in an emergency situation of A.C.
Supply failure. This arragement ensures an uninterrrupted
D.C. Supply to the connected load at all times - by the
Battery Charger in case of A.C. Power Supply availability or
by the Battery in case of failure of A.C. Power Supply.

Is This Answer Correct ?    52 Yes 10 No

why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / muhammad mustaghas

1) The operation of monitoring devices such as relays and
the tripping mechanisms of breakers require an independent
power source, which does not vary with main source being
monitored.Batteries provide this power source for the
successful operation of switching and control devices in
power protection system.
It is therefore necessary to ensure that batteries and
charges are regularly inspected and maintained at the
highest possible level of efficiency at all times to enable
correct opeartion of relays at the correct time.
2)UPS means uninteruptable power supply which accept AC as
input and convert this AC into DC for the storage purpose
and when require AC supply then again it convert DC into AC
for its out put terminal.Basically UPS is used to stored
the energy in from of current to fullfill the requirement
for emergency supply but batteries only provide the DC
power supply to its load and can store and supply the
limited amount of power.

Is This Answer Correct ?    21 Yes 4 No

why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / amit khamesra

In lieu of a more reliable power supply source, DC supply
is used in place of normal AC supply. If there is a
blackout, AC power will not be available n the electrical
protection devices will not operate. To avoid any such
situation, DC supply is used. DC supply is provided by
batteries and charger is used to keep the batteries healthy
by trickle charging the batteries in Float / Boost mode as
required. UPS is an uninteruptable power supply which uses
converter inverter set. AC input is first converted to DC
and again converted to AC. The battery bank installed for
UPS is connected in between converter inverter set so that
if AC supply to converter fails, battery comes on load and
supplies DC to inverter for maintaining the AC power supply
at output end.

Is This Answer Correct ?    17 Yes 9 No

why Batteries & Battery chargers are used in substation? what is the different between UPS &am..

Answer / tarun aggarwal ymca

In AC substations if AC power fails, for tripping of Switchgear an alternative supply is needed. This supply is DC supply from Batteries. AC supply can not be stored where as DC can be stored in batteries. Hence all circuit breakers are with DC voltage coils. In case of a line to line fault or line to earth fault the incoming / remote breaker needs to be tripped. At this point AC is not available and hence DC is used. 
While AC over voltage or Under voltage are abnormal conditions and hence AC supply is present hence AC coil can be used. 
For charging of battery, battery charger is used. Charger takes AC voltage, steps down and rectifies in to DC voltage and supplies charging current to battery. 




UPS (Uninterrupted Power Supply), consists of a rectifier, battery and inverter and its output is AC supply. During utility power supply fails, this UPS supplies AC voltage to instruments for monitoring important parameters. But this also depends on Battery. Hence efficiency of UPS is low, as well as reliability is low due to more components. Hence using battery is better for tripping functions in protection circuits. In case AC power fails for longer duration standby DG set is started for charging battery.

Is This Answer Correct ?    10 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Define reserve-generating capacity?

0 Answers  


What is harmonics and how the 1st,2nd,3rd etc harmonic levels

2 Answers  


What is CCTV System???Applications........

16 Answers   Emerson, Honeywell, Joyalukkas,


It is being often experienced that due to single phasing fault of any source transmission line of any closed loop synchronized circuit all the power transformers with primary stared trips but the power transformer with primary delta wont, why ?

1 Answers   MSEB,


what's float charger and boost charger? why it's used?

2 Answers   APCPDCL, PTCL, Rolls Royce, Siemens,






Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.

0 Answers   Piramal Healthcare,


where they are using surge arrester and lighting arrester? how they connect? what is the purpose of that?

1 Answers  


How the electric train gets the supply of electricity? What is the return path of the current?

7 Answers   NTPC,


What is the reason that the humming sound is coming from the induction furnace panel?

0 Answers   SKS Microfinance,


Why 1/3 is used in symmetrical components?

0 Answers   ABB,


How can step up and step down process in power transformer

1 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd,


over frequency is the protection of turbine or alternator?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)