Why 3 over-current and 1 earth fault relay is used on
primary side of transformer? Why 2 over-current and 1 earth
fault relay in used on secondary side of transformer?
Answer / ronik
1)The reason when a double line fault occurs on secondary
side then if the transformer is of DY11 type then if 2
over-current relays are used on primary side instead of 3
O/C relays then the phase in which no relay is placed will
carry double the fault current and the in current in the
either phase will be low enough that a relay can pick
up...and meanwhile the damage will be done to the system...
2)Moreover the ground fault on the secondary side will not
have any effect on the earth fault relay on the primary side...
3)on secondary side each and every fault will be detected by
the 2 O/C and 1 earth fault relay easily...
Is This Answer Correct ? | 4 Yes | 4 No |
where is core-type and shell-type construction suitable for transformers ?
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
DRAW THE DIFFERENCE BETWEEN GROUND AND NEUTRAL IN BOTH SINGLE PHASE AND THREE PHASE?
What is MS-EXCELL?
why the manufacturer provide M and C terminals ? why they will not internally short them ?
how to apply b license to c license in tneb
grr resistance & contrator malt continuous
How to put breaker in service / test position.
What is inductance?
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
What are the three major categories of error?