Why 3 over-current and 1 earth fault relay is used on
primary side of transformer? Why 2 over-current and 1 earth
fault relay in used on secondary side of transformer?
Answer / ronik
1)The reason when a double line fault occurs on secondary
side then if the transformer is of DY11 type then if 2
over-current relays are used on primary side instead of 3
O/C relays then the phase in which no relay is placed will
carry double the fault current and the in current in the
either phase will be low enough that a relay can pick
up...and meanwhile the damage will be done to the system...
2)Moreover the ground fault on the secondary side will not
have any effect on the earth fault relay on the primary side...
3)on secondary side each and every fault will be detected by
the 2 O/C and 1 earth fault relay easily...
| Is This Answer Correct ? | 4 Yes | 4 No |
In a three-phase full converter, every SCR conducts for a.60deg. b. 120deg. C.180deg. d.90deg
what is circuit recombiner and how it is different from circuit breaker
what is the frequency standard with tolerance level for India?
what will happen if we pass a dc current through a ac bulb of 60 watt.The dc current is half ac one
When color of silica gel will gets change from blue to pink from Top to bottom?
will 1050kva DG set withstand for back charge of 16MVA transformer
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
how power trnafor from 1 point to another point in bus bar ya transmission line( voltage trnasfer from 1 point to another poin)
What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.
what is rocking arrangement in arc heating
When a fourth resistor is connected in series with three resistors, the total resistance
Why do we have 110V, 230V, 415V etc. in electrical transmissions? Why not 100V, 200V,400V?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)