How to calculate the cable size (XLPE)for suitable to 120KW
load (if Motor or heaters etc)
Answers were Sorted based on User's Feedback
Answer / prakashchandra rana
for 120kw motor flc is 180amp at .8 pf so if we run this motor
on star delta starter we will use two numbers of 150sq.mm
cable from starter to motor and its main power cable will be
of 300sq.mm.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / subhash t p
this load should conected with 3 phase
120*1000/440=273amps
we can use 300mm2xlpe cable.
Is This Answer Correct ? | 9 Yes | 8 No |
Answer / malleswr
for 120kw motor flc is 220A so cable size taken 1.5 times
to flc ie 330 300mm2 cable use
Is This Answer Correct ? | 5 Yes | 6 No |
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
why ac ratings are in tons?
How to reduce -234126219.6403 MVAr generation and by what?
What is third harmonic?what is the effect of it?
WHAT IS THE DIFFERENCE BETWEEN A DC MACHINE OUTPUT AND RECTIFIER OUTPUT...
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
what are the compensations considered while designing a transmmision line.
Pleasd Tell Me..... In Generating Stations Why The Generation Of ELECTRICITY Is In 3 Phase Form?? OR In Generating Station Why We Generates The ELECTRICITY In The 3 Phase?? Why Not In The 4 Phase, 5 Phase Or 6 Phase Form??
how synchronous generator can be used as synchronous condenser?
why ht alternators gland plats using brass?
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
hoW to select a CT?