What is the rating of your capacitor bank at your company.
Answer Posted / ashishpalakkadan
The size of your capacitor bank will depend upon your load, existing power factor and your required power factor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
DG Earth Value?
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
A ii kv 1200 A Breaker combination fixed in a cubicle. How many ampere Fuse is required? If fuse is not using, Why?
1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to confirm its base capacity?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
What are the material used for resistor?
Is single load(eg: three phase motor) having all the components like positive,negative,zero sequence components during fault condition?
can we use trip light with bus coupler?
33kv substation lay out details & line to line & line to earth measurements
what is ATS & RING MAIN UNIT in Distribution System?And its Function.
1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?
what happens if dc supply is given and the remedies for it.
substation+ plc system
What is the end effect of linear induction motor ??