What is the rating of your capacitor bank at your company.
Answer Posted / m.reda
cap.bank used for p.f correction to compensate reactive power supplied from utility to reduce losses in power through t.l so we use cap near load in parallel ....how to calc cap rated
Quncorrected=pxtanφ1
Qcorrected=P×tanφ2,
where P- real power. From this we find the required Qc:
Qc= Quncorrected-Qcorrected=P×(tanφ1- tanφ2)
Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
State uses of different types of stsrters with different capacities of motors as below: a. up to 5HP b. above 5hp to 10hp c. above 10hp to 20hp d. above 20hp
how to measure dc earth leakage current?
how harmonics generated in induction furnance? how minimise it?
What are the protection required for Transformer, motor, Line, Generator, capacitor, that all i have to refer which standard?(Like Transformer detail IS 2026)
Earth leakage relay basic knowledge principle
how to select battery for 15 KVA UPS with formula
how to find the torque of the single phase synchronous motor by doing an experiment
Hoe do calculate the Cable size for Amps rating ?
why power not passes in plastic and rubber material
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
Is potential difference materials property ..? if yes tnen how.. explain brifly.
what happen if drive input fail momentry at 48.5 HZ frequency?
what r the safety measures in UPS ? explain all?
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?