Why we use DC for charging of Batteries??Why not AC
Supply???
Answer Posted / ramachandran n
If we are using AC supply,in positive half cycle battery
will charge and in negative half cycle battery will
dischage so finally there is no charge.
But in Direct cuurent, there is no phase angle between V
and I & so no power factor also.
all are in phase ,so in DC only we can charge the batteries
| Is This Answer Correct ? | 63 Yes | 2 No |
Post New Answer View All Answers
What are the protections for safe running of electric generator?
1sq mm dc powr cable can carry how much dc currnt
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
What is routh hurwitz stability criterion?
hai now i am working as a electrical design engineer in construction field can i get a job in oil and gass field or power plant project as a electrical design engineer?
How to calculate capacitor bank size at a load 800kVA.
Vaccum circuit breaker
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?
Why field rheostat is kept in minimum position?
What do you understand by oldham's coupling ?
when the time of backcharging the transformer three phases only enough or three phase with neutral is must.from these which one is the best one.