if we supply DC power to AC transformer then what its result?

Answer Posted / kedam .koteswar

if we supply DC power to AC Transformer the primary winding will burn,it not effects to secondary winding because the AC transformers are magnetically coupled not electrically. Transformer works on the principle of mutual induction of two coils.

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

i need the curve duty cycle and amper for (150 kva @50% dyty cycle) transformer turn ratio :19 and vin 400

1632


how  do you choose the cable size as per amps rating & the voltage drop for the same.

1344


How to do bus bar short circuit calculation for 230KV/11kv, 60 MVA Substation?

4265


Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?

676


Single line diagram for dbb (double bus bar)system.

1479






will 1050kva DG set withstand for back charge of 16MVA transformer

1465


what is POTT and PUTT explain?

2818


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

1980


what causes contact chatter when there is no demand on the air conditioning unit?

1618


show the single line diagram of star delta starter with single phase preventer

4112


I Want randstand placement papers

1368


what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value

1663


how to select size of hardware for linking aluminium busbar is it depend on area of busbar or current flowing through bus bar

1542


How does PLC work for sychronising of Two or more DG sets?

1646


What is the rating factor for copper cable ( Specific value according to the type of laying ) & the voltage drop?

1422