What is mean by vector group? For what purposes we doing
vector group test in transformers?
Answer Posted / satya dev
In the 3 phase AC systems all the phases are having Phase
displacement called electrical Angle.In the case of
transformers the windings are connnected in special Faison
called Vector group. DY11, DYn11 are the vector gruops
which are generally used in India.Testing of vector group
is only to test the electrical of Connected Phases in the
Transformers.
Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
What is T’Q and X’Q and X’D ? and what is saturated as well as unsaturated ?
What is step signal?
How to decide no. of Step and Kvar for APFC Panel 40 kvar MD: 33.12 KVA Avg pf : 0.8540
How impulse levels are calculated that for 11kV impulse is 75kvp, for 24kV impulse is 125kvp ?
redundant connection in contactor?
Formulae for calculating the transmission line losses for different voltage levels
what is earth pit , how we can measured it, what earth rods reference
How RTCC panel is working and give single line diagram for RTCC with transformer?
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
What is the effect of pd controller on system performance?
What is difference between Harmonic and Non harmonic Capacitor Bank?
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?
what is the saturation point of crgo lamination.
Why i receive the GCU fault in my DG Sychronization panel . what all the factors considered for this fault .