sigal phase supply is 230 v ac two phase supply is 415 v ac
then why three phase supply having supply is 415 v ac why
not 690v ac
Answer Posted / neeraj pandey
voltage value is the Line to Line Voltage. Line to line
voltage is the voltage between any two phase lines.
In single phase there is one phase and another is earth wire
and voltage between them is 230V approx.
In two phase the line voltage is 1.732 times of the single
phase voltage and the value is 415 V approx.
In three phase system the value of voltage between two
phases are taken which is same as two phase system.
if we take the voltage diff between all three phases it will
be ZERO..
Is This Answer Correct ? | 11 Yes | 0 No |
Post New Answer View All Answers
33kv substation lay out details & line to line & line to earth measurements
what is lrs tank water resistance.
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end
How to Calculate Transformer Earthing Electrode Rod Size both Body and neutral Earthing ? Any Standard Formula? Please Suggted
what is destructive and non-destructive testing of welding
pls tell me about ups internal connection & we have given only 3 phase supply to ups system how get 4 wire (R Y B N )
Why LED light has advantage of rapid reflection ,although other lights alse reflect.? and this light is considered to be best for transmission usage in case of Free optics
What are the uses of stepper motor?
What is the difference between vector surge relay (78) and Pole slip relay (98G)
What is state space method ? Why its used ? Can it applicable on linear, non-linear, 1st order, higher order, homogeneous, non-homogeneous, open-loop , closed loops , stable & unstable systems ?
What do you mean by an instrument transformer?
11000volt DG set carnt kaise banvay
What is reverse power relay?
What is cable tray, its type, and its support?
What happens when ac supply is given as excitation voltage instead of dc supply