What is the Difference Between MCCB & ACB & VCB
Answer Posted / navneet kumar
MCCB"Moulded Case Circuit Breaker" is based on expension of
bimetalic strip due to thermoelectric effect.
In ACB "Air circuit breaker" two contact seperate by the
force of spring in air.
In VCB "Vaccum Circuit Breaker" two contact seperate by
force of spring in Vaccum.
However, The application of all MCCB, ACB and VCB are same
i.e. to isolate the faulty circuit from healthy one.
Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
why ten delta testing is carried out on power transformer
how does the thyistor work in dc drive?
why and where we use early make & late break contacts in protection?
Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
Electrical Engineering
what happen ehen synchronisation is done at below rated speed
how does an encoder work???
15hp motor wound by 0.9mm & 0.95mm magnet wire. at no load test it draw 4.2A current. Another motor with same condition draw 9.2A current. How can that occur? pls help
state types of reflectors in illumination engg. ???????
What is your acheivements
if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .
State how to produce a constant rotating field by application of alternating currents to stator armature of a three-phase squirrel-cage induction motor
what is the soft starter principle? how is connection diagram? what is the procedure for checking the connection?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.