how do find power factor in practically and what it means?

Answer Posted / abid ali khattak

For the practically experiment of power factor we need to
connect the two type of same Wattage AC load with the
circuit. 1- inductive load. 2- Resistive load. and then we
need to be measured the current of both laod. We will find
that the inductive load getting more current then resistive
load.( lagging & Leading)
Beacause of inductance which induced in the inductive load.
which always oppose the provided EMF.

Is This Answer Correct ?    12 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

we specify current in case of feeder but in case of distributor voltage, why?

1379


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

1406


What facility we get after CT secondary earthing and how?

1721


defination of lines

1538


wat is the current produced in a 5000v megger? when the positive and negetive terminals are touched on our body get s shock?

1496






how does an encoder work???

2040


what is die electric strnth of transformer ?

1652


why most of junction box vendors providing T5/T6 Temp class jb's for T3 area any special reason?

1633


TRANSFORMERS WITH DC SUPPLY

1522


what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth

993


How does an oscillator differ from an amplifier?

662


why starting current is high and resistance is almost 0 during the starting of motor dc motor...?

1285


what is the thumb rule for determination resistance of resistor?

1816


LT cable fault chaecking equipment and to find out the distance at what distence it failure . Name and where it is available?

1677


what is level 2 automation?

2716