Please tell me 1 ton = How many Kilowatt (Electrical)
Answer Posted / mohamed hamid
We can under stand to things from the question:
1- If you mean by kW electrical that how many electric kW consuming for A/C unit for 1Ton? Answer, It depend on the manufacturer and design of the A/C unit But you can take it 1.2 kW for safely design for power cable, preacher and other electrical devices.
2- If you mean by kW electrical that, how many kW(cooling or heating power) in Ton refrigeration? Answer, It is as told before by our colleges
1 kW of cooling/Heating = 0.284 RT or
1 RT = 3.52 kW of cooling/Heating
| Is This Answer Correct ? | 0 Yes | 2 No |
Post New Answer View All Answers
give some advantages and disadvantages of combiniing the session, presentation, and application layer in the osi model into one single application layer in the internet model
Zone of protection and tripping scheme of arc protection relay.
what is capacitor voltage transformer?? how it is different from potential transformer?
Why temperature rise is conducted in bus bars and isolators?
What is the high series capacitance winding on high voltage power transformer ?
What is FTA card? How it works?
How we can come to know the substation range,without go through any name plate ?
Which device of PlC does share load between DG sets when DG are running in perallel?
Transmission voltage is kept 11KV,33KV,66KV,132KV,220KV due to form factor. What happen to 400KV and 765KV transmission voltage?
how we can calculate the efficiency of a diesel generator ?
What is frantic effect?
How seriving & testing of the HT & LT breakers are done. What are the standard Ir values on which we can come to know the test is passed or failed?
What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?