How do you connect the capacitors on polyphase circuits?
Answer Posted / h r rajyaguru
In three phase load the capacitor bank is connected for improving the power factor (P F). The rating (KVA and V) of the bank can be calculated depending on the existing system voltage and up to which P F we intend to improve. The ideal location of this Capacitor Bank is near to the load. For large size motor / load separate circuit breakers are to be used for switching the said Capacitor Bank. The motor and the bank are to be closed / opened simultaneously. Some times Capacitor Banks are connected with the Motor Control Center (MCC) or Power Control Center (PCC) for improving the P F of the system. The voltage rating shall be 10% higher than the system voltage.
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
What is the differentional relay...what is the work of this in power Tx. how it is works..
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured
Fantio of tranformer
why incomer bay is required before transformer bay if there are more than 1 nos. of transformer bay.
What are the different power system losses and how can it be eliminated?
what is the Transformer Impedence?How can calculate?
when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
1.what is the funtion of chiller primary & scondary pumps. 2.what is the use of distribution lines & Types. 3.what is the use the thermal power stations & how much capacity.
Under wat condition statcom operates as an inductor for the transmission line?
How can we increase fuel-power ratio of any DG set?
How dia computation perfomed in cold rolling mills .
how line turns ratio changes in 3 phase with change in connection
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
oltc of a transformer, how it works? and what are the equipment consist of describe briefly?