Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

In 1000KVA Transformer why does we connect HT with delta
connection and LT with star connection.Illustrate by showing
formula?

Answer Posted / bikki

In HT transformer, the primary side has less voltage stress since it is a step up transformer. But the voltage on secondary side will be high and hence the stress will be also high.As a result, the winding insulation requirement will cost a lot if the connection was Delta on secondary side;because in delta phase voltage=line voltage.
But if the secondary connection is star, then phase voltage will be Line voltage/(sqrt(3) which means the winding has to withstand less voltage stress and hence less insulation is required.Hence lesser cost.

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

difrent between vcb acb sf6 and mccb breakers

5536


What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?

1940


What are the effects of electrical faults?

1075


What is meant by coupling capacitor?

1130


Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?

1784


11000volt DG set carnt kaise banvay

1726


in non technical way how can u define POWER FACTOR??

1875


What is the effect of positive feedback on stability of the system?

1713


high voltage transformer input voltage,current and amps rating..distributed transformer input voltage,current and amps rating...

2065


What is the difference between hot and cold loop testing?

1201


How do I calculate/select Droop CT ratio for various capacity of generators?

3708


what's the requirement of Dy11d0 connection of 3 phase transformer?what's use of it?

8038


Explain the laying procedure and laying depth of submarine/subsea power cable for 220/400KV system? Also available cable diameter?

2156


Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer

1903


What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance

2045