Answer Posted / manish
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
WHY RATING OF VCB NOT LESS THAN 630A
what is induction furnance? how many phase supply given io its coil for 15 or 20 ton furnance?
what type of questions are asked and howmwny questions belong this catagory?
i am studying in final year can i allowed for 23rd UES of Indian army
What is the actual calculation for transformer short circuit test?.
How will you define capacitance?
how to check regenerative load in drived motor
How relay works, reverse relay, master relay, os relay, earth fault relay and what is its setting point
What is the emf equation of a transformer?
hr round
Cb closed condition if there is a tcs fail whether cb will trip or not
what are the interview question asked in wind mill about electrical
Difference between Lugs and Thimbles
How is the connection of the tap changer on the HV side been made?