How to Select a Transformer Rating ?

Answer Posted / naveen

because total losses depend upon cu losses and iron losses cu losses deped on current and iron losses depend on voltage so total losses will be volt amp thats why rating in KVA

Is This Answer Correct ?    8 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

EXPLAIN THE ESSENTIAL FACTORS WHICH INFLUENCES THE CHOICE OF SITE FOR A HYDRO ELECTRIC POWER PLANT

1548


What is the basic of DTH.

1861


Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.

1553


How 48-relay (incomplete sequence) functions?

3544


How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors

1470






Is single load(eg: three phase motor) having all the components like positive,negative,zero sequence components during fault condition?

1351


What is real time power factor control panel(RTPFC)?

3818


A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.

911


what is the Transformer Impedence?How can calculate?

1451


Refernce currents are to be generated using refernce cueernts how can this be done

1777


-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.

1563


WHY L-G FAULT IS MORE SEVERE IN TERMS OF RRRV?

2710


what happen when increase or decrease size of lamp,light.glass.

1485


we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?

1486


How will you define capacitance?

698