what are the differenc between vcb and sf6 breakers
Answer Posted / jayakumar v
VCB MEANS VACUUM CIRCUIT BREAKER 11 TO 33 KV IS APPLICABLE.
INSIDE OF THE BREAKER HAVING AN ONE VACUUM INTERRUPTER WITH CONTACTS. HERE VACUUM IS AN ARC QUENCHING MEDIUM. INSIDE OF INTERRUPTER VACUUM HAS BEEN CREATED BY MECHANICALLY (MANUAL) OR ELECTRICALLY(THROUGH DC MOTOR).
SF6 BREAKER MEANS SULPHURHEXA FLUORIDE BREAKER. IN UPPER SIDE OF THE BREAKER HAVING AN GAS POLE ASSEMBLY. INSIDE OF THE POLE ASSEMBLY HAVING AN MALE & FEMALE CONTACTS. ALWAYS MAINTAINING 3.8 Kpa PRESSURE INSIDE OF POLE FOR 33 KV LINE.THIS BREAKER RANGES UPTO 750KV.
Is This Answer Correct ? | 3 Yes | 2 No |
Post New Answer View All Answers
What is principle of Floroscent tube 36watt.
What do you mean by an instrument transformer?
What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
What happens if we connect a single phase energy meter in reverse polarity.
what are the condition that makes hooter blow?
What is expention fastener (Fan)
I want to ask that is there any relation between current denesity of copper and material purity. also is ther any standard which defines the standard current denesity of material.
relation between power station capacity and voltage level?
What is resistance reading of earth copper rod with grid and without grid?
why the voltage and current in a long transmission line are called travelling wave?
What is vaccum currcuit breaker.define with cause and where be use it device?
How much voltage we need to apply in 33kv cable during hipot test of cable
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
What are the various types of BUSBAR Schemes? explain each