In 1000KVA Transformer why does we connect HT with delta
connection and LT with star connection.Illustrate by showing
formula?
Answer Posted / siddhartha agrawal
Generally HT side there is only three phase available while
LT side we require neutral. So we connect LT side Star
connection to use phase to phase voltage (415 volt) and
phase to neutral voltage- single phase load (240-220volt).
Generally HT side there is only 3 wire to reduce the cost of
transmission wire cost.
| Is This Answer Correct ? | 8 Yes | 1 No |
Post New Answer View All Answers
how to calculate energy of 3-phase motor?
Whether the vacuum contactor requires Short circuit protection?If No,why?
What is the unit audit? if our Max demand is something and we found much more unit then how to improve our max demand?
In a single how much maximum current and watts using
Is it possible to use a S1 duty class motor for crane application (S4)? If not, why?
Working of microwave oven?
i've iocl interview.. if you know the interview process please give me information..
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
what is PID control in VFD drives?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice
WHaT IS THE CONCEPT OF INDUCTION LAMPS IN MODERN LIGHTINGS, and HOW IT WORKS TO EMIT LIGHT ( AS NO ELECTRODES ARE PRESENT ) ?" COULD INDUCTION LAMPS CAUSE INTERFERENCE WITH COMUNICATIONS INTO A STORE USING INDUCTION LIGHTING ? WHAT IS THE BENEFIT OF USING THE LOW FREQENCY INDUCTION LAMP , VERSUS LED , AND VERSUS FLUORESCENT, AND VERSUS ANOTHER KIND OF LIGHTING . THANK yOU MOISES GUINDI
How time response of the system is divided?
why we used ZNO in Lightning arrester.
What is the equivalent circuit of a transformer and its vector diagram?
Why should we hire you over the others waiting to be interview?