what is the difference between MCCB and SFU in terms of their
application?
Answer Posted / monty
Fristly understand
MCCB- module case circuit breaker & SFU- switch fuse unit
SFU- it is a combination of a fuse and isolator
MCCB-it is just like a MCB(miniature circuit breaker) but there is a small difference we can vary the range of MCCB means if you have 100A mvvb than you can use it for less than 100 A also but in MCB it is not possible so we can say that MCCB is a variable fuse.
Is This Answer Correct ? | 18 Yes | 12 No |
Post New Answer View All Answers
If Dg set load increase 25%, How much increase fuel Consumption (15 kva 2 cylinder DG set)
i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.
what is star delta starter? how it works? give its control and power diagram.
What are the roles and responsibilities of electrical engineer in cement plant
What is current divider rule (cdr)?
How to decide CT & PT ratings for a given transmission line carrying some rated voltage?
What is the abbreviation of NGT panel
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
what is difference between speed mode and torque mode in motor?? explain in simple words please.
Define transfer function?
What consists of 2 or more thermocouples to be connented series?
how many electricity poles are there and what are the names and their sizes.
we specify current in case of feeder but in case of distributor voltage, why?
What are the specifications for conducting earth leakage test as per IEC standard?
what is the isolation transformer. what is the isolator?