1. what type of winding of slip ring ac induction motor
rotor and why. 2. how the heating element use in two phase
(415 volt)and what rating of element, you prefered.
Answer Posted / k.prakashchandra
Regular 3 phase windings for both stator and rotor.I don't
think heating element is provided .A low voltage is applied
to windings with help of a transformer so that a current
equal to or less than full load current is circulated to
warm up the windings .The voltage and capacity of this tr
depends on the rating of the motor.As the stator is normally
delta wound, one coil gets the full voltage and other two
50% each.As you press the start button ,the transformer gets
disconnected or you can switch it off beforehand.
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
how to calculate the step resistance for slipring induction motor,how you deside the no of step for that?
what is the principle of operation of tungstun bulb ??
what is advertised hop count
What are the three constants associated with a steady state error?
1.What will be stored in online ups EPROM IC?
Why an ac systems are preferred over dc systems?
State kirchoff current law?
what questions are asked in the interview for the post of an electrical maintenance engineer in FMCG companies?
Help need in transformer !? Hello Friends The parameters of 2300/230 v 50hz t/f is R1=0.286 ohm R`2=0.319 ohm Rc=240 ohm X1=0.73 ohm X`2=0.73 ohm Xm=49.2 ohm Secondary Load impedance ZL=0.387+J0.29 solve the exact equivalent circuit with normal voltage across primery.. I know every thing but i cant find CURRENT I1=? and I`2=? Please help me give solution or only Formula please please...
Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).
WHAT IS VCB SAFETY
how is working bearing heater?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING) I O (current operating)?
what is thermal resistance of PVC Cable.
Why AC & DC capacitor are use in UPS ??????????????????