1. what type of winding of slip ring ac induction motor
rotor and why. 2. how the heating element use in two phase
(415 volt)and what rating of element, you prefered.
Answer Posted / k.prakashchandra
Regular 3 phase windings for both stator and rotor.I don't
think heating element is provided .A low voltage is applied
to windings with help of a transformer so that a current
equal to or less than full load current is circulated to
warm up the windings .The voltage and capacity of this tr
depends on the rating of the motor.As the stator is normally
delta wound, one coil gets the full voltage and other two
50% each.As you press the start button ,the transformer gets
disconnected or you can switch it off beforehand.
Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
How many types of instrument cables are there?
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
How to select a contactor? How many types of contactors are available
why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?
how does ELR works? explain
What is marx circuit?
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
how to calculate the Neutral transformer impedance?
WHAT IS THE DIFFERENCE BETWEEN AN ACB & mccb 7 WHAT IS THE CRITERIA WHEN TO USE WHICH OF THE TWO
what is the use of vcb & isolator in substation?
Why a Permanent Magnet Generator has higher frequency as compared to frequency of main alternator?
what is the stear deltaprinceple?
What is the RME and explain the full form and what is the RME work?
How to calculate Air conditioning capacity for a telecom BTS shelter?