Do you know how to measure the earth resistance? if so
explain it
Answer Posted / ahmad abu alrob
Normally no meaning for earth resistance, we use a
measurement of resistance in a definite location to
calculate the Earth Resistivity which can be used for the
calculation of Grounding/ Earthing mesh resistance.
Measurement can be done in one of the following:
1- Normal Volt/ Ampere method: Inject current and measure
voltage , then you will got the resistance.
OR
2- Wenner method using 4 electrodes: You should use the
equipment especially used for this purpose, and you should
follow the instruction attached with the equipment.
OR
3- Using Schlumberger method applying 4 electrodes: same
equipment used in 2 but different calculation applied.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
Purpose of providing neutral isolation panel for parallel operation of diesel generator
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
1.4 What is meant by CT knee point voltage and how would you determine it
Do closed loop systems require manual input?
hi friend i am going too attend for hpcl in this month please help me by sending written test question papers i am in the stream of E.E.E
What is dynamo?How it works and what is the function of dynamo in a DG.
what is servo motor and how to work it.
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
I WANT BHEL PREVIOUS QUESTION
How 48-relay (incomplete sequence) functions?
What are the different circuits in thermal power plant?
What is error of a measurement?
what is tri state logic gate
physical identification of HT & LT panel