What is the d/f between DOL & star delta starter & automatic
star delta starter?
Answer Posted / suresh pulipati
In case of Star Delta starter the motor intially will run
in star connection and when 80% of rated speed picks, the
motor change over to delta connection. With this star delta
connection we are able to reduce starting current by 1/3 of
DOL starting current and starting torque also.
| Is This Answer Correct ? | 226 Yes | 33 No |
Post New Answer View All Answers
I am going to appear for the RRB Chennai junior Engineer online exam. Please send me the previous exams question papers (also solved) to my mail id: rrkhandhar@yahoo.com
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?
What happen to generator if i have unbalanced load?
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
which IS or IEC is used for earthing,breakdown voltage of transformer oil, hv/pd testing and all type of electrical testing
what is the function of capacitor duty contactor in an capacitor panel???
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
what is star delta starter? how it works? give its control and power diagram.
how to determine ct ratio in ht vcb?
how to measure the current by compact digital equipment with dislay which fit inside any equipment
how can you calculate fault level ?
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
Batteries used for electrical energy storage are a. Laclanche cells b. Edison cells c. Lead acid cells d.any of the above
how to calculate the distance relay faulty zone?pls explain?
explain the functions of main isolation switches