What is the basic difference between earthing, ground and
neutral?
Answer Posted / rabi
Neutral- it is a point where the sum of the current meeting
at that point is zero. E.g. in three phase star connected
winding the neutral is the point where all winding is
meeting at a same point obviously at normal operating
condition.
Ground- ground and earth both are same term. it may be a
reference point for in an electrical circuit from which
other voltages are measured, or a common return path for
electric current, or a direct physical connection to the
Earth.
Earthing -it is nothing but the process of connecting all
the neutral points of the equipment and non-conductive
exposed part of the metal structure to earth.
| Is This Answer Correct ? | 141 Yes | 19 No |
Post New Answer View All Answers
what is the purpose of high speed earth switch in gas insulated substat
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
What is oscillator circuit?
What id difference between power and energy?
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
explain wiring system
What is servo motor? what is its purpose?
how to select correct size of power cable for inverter duty motor
whats the existence of reactive power and when it arises?
if a.c supply is given to the motor,, what happen?
how to calculate the surge level of surge suppressors related to the SF6 cicuit breakers?
Zone of protection and tripping scheme of arc protection relay.
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
anyone please send transformer parameter design formulas & details of tap changer ? plz i have interview this week its more helpful for me ?
Is there a standard depth of gravel fill in Substation Switchyard? Please give a design/drawing. Thank you.