what is the difference between earth and neutral?
Answer Posted / jaikol enim
earth con act as electron bank ie we can give and take
whatever we need
where as neutral there is a limit that depends on the system
| Is This Answer Correct ? | 14 Yes | 6 No |
Post New Answer View All Answers
If we have to feed a housing complex having load 8MVA, than what would be the better option, either we first step down 33kv supply into 11kv & than 430v or we proposed no of 33/.44 kv transformer, also which option is economical?
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
when we have to purchase the transformer by own i.e how much load will preferred HT connection?
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
What size cable (based on voltage drop) is required to supply a 40 A three phase boiler if the wiring system is 75V single insulated cables installed in non-metallic rigid conduit 56m from the main switchboard? Voltage drop in the consumer's mains is 8V.
what & how to check the lightning arrester
How to calculate the Harmonics losses in terms of cost/unit.
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
what do w do when the output of generator is fluctuating?
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
Explain the process of commutation in a dc machine.
why we use copper earthing for neutral while for body GI.
What are the advantages of hydropower?
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
How to work E.L.C.B and how to connect in circuit.