adspace
What are the types of Transformer? Name them.
Answer Posted / amit upadhyay dscl
The type of t/f is
1. core type
2. cell type
3. berry type
| Is This Answer Correct ? | 41 Yes | 6 No |
Post New Answer View All Answers
what is the condition for YnD11
sir, I am from EEE branch.On feb 17 iam going to write an Exam for hindustan petrolium corporation Ltd.So plz send me the written exam pattern/Q's/interview questions.please mail to eee_dharmendra@yahoo.com
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
Draw a SLD of DG distribution up to main LT panel?
what are the values of VRY,VYB,VBR,Vry,Vyb,Vbr,Vrn,Vyn,Vbn for Magenetic balance test of 100 KVA and 63 KVA Distribution transformer
Draw the line diagram of diffretial relay connected to transformer?
what is mean by restructuring power system?
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.
Can Anyone Answer anyone of these ? Q1) why direct SOLUTION of Load Flow Studies in Not Possile ? Q2)Why majority of Buses in power system are load buses Q3)Why one of the buses in Power system is taken as reference bus (slack or swing) Bus ? Q4)Bus Admittance Matrix is a sparce (means it contains some zero elements ) matrix , give reason
TO CALCULATE THE RESISTANCE OF GRR OF HT MOTOR 400KW WHEREAS STATOR VOLTAGE 6.6KV AND ROTOR VOLTAGE 705V AND ROTOR CURRENT IS 346A.
Anybody tell me about modbus hex address of l&t trivector meter er300p??I want to read voltage,current,kwh etc via rs485...If anybody have a manual then send on my mail..Brijeshmodi18@gmail.Com
Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault