what is the difference between megger and earth tester?
Answer Posted / mustakul
megger is an instument which in addition to measurement of
high resistance can be used to test the quality of the
insulation at or above its operating voltage.
whereas earth tester is used to measure low earth resistance
| Is This Answer Correct ? | 197 Yes | 18 No |