In Aeroplane what circuitry or method use for earthing?
Answer Posted / ramesh gaur
negative terminal of dc source is connected to the airframe
only positive wire is taken to the equipments.airframe is
used as ground (return path)
| Is This Answer Correct ? | 15 Yes | 5 No |
Post New Answer View All Answers
What is called grain-oriented laminations?
What is core CT & it's function?
substation+ plc system
Can an inverter be used as a converter? How?
cc of scorpio?
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
what is the clear formula to calculate cable size for a load
along with technical test papers
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
1 hp is equal to how much watt?
The electromagnetic torque developed is proportional to what in a D.C series motor?
On Which Pressure PRV is operated.
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
what can be the causes of capacitor start motor having a higher current that its actual
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.